Robert E Lee Posted March 8, 2011 Report Share Posted March 8, 2011 I did an inspection last week where the panel board was mounted directly to the concrete block wall, this panel was installed 5 years ago and there was evidence that the lead anchors were corroding due to moisture. I called for an electrician correct saying that "The panel needed to be mounted on a wood panel". I am getting kick back from the electrician saying that code does not require mounting on a board. I can't recall seeing a panel that wasn't mounted on a board of some kind. The only code reference I find is 312.2A that calls for a 1/4" air gap between the enclosure and the wall. Any other thoughts? Click to Enlarge 39.14 KB Click to Enlarge 45.5 KB Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted March 8, 2011 Report Share Posted March 8, 2011 Does the back side of the panelboard have those "dimples" that hold the back side away from the foundation? Whether or not min. standards have been met, I'd recommend repairs based on the damage that's occurring. Screw min. standards when it's not working. Link to comment Share on other sites More sharing options...
Marc Posted March 8, 2011 Report Share Posted March 8, 2011 2008 NEC, 312.2: In damp or wet locations, surface type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box.... Little water seems to have entered the enclosure, but the damage is already done. Needs to be fixed before it falls off the wall. Marc Link to comment Share on other sites More sharing options...
Scottpat Posted March 8, 2011 Report Share Posted March 8, 2011 I did an inspection last week where the panel board was mounted directly to the concrete block wall, this panel was installed 5 years ago and there was evidence that the lead anchors were corroding due to moisture. I called for an electrician correct saying that "The panel needed to be mounted on a wood panel". I am getting kick back from the electrician saying that code does not require mounting on a board. I can't recall seeing a panel that wasn't mounted on a board of some kind. The only code reference I find is 312.2A that calls for a 1/4" air gap between the enclosure and the wall. Any other thoughts? Click to Enlarge 39.14 KB Click to Enlarge 45.5 KB I think the electrician is correct, but I'm not 100% sure. Oh, by the way you have a great name! Link to comment Share on other sites More sharing options...
kurt Posted March 8, 2011 Report Share Posted March 8, 2011 A couple things..... Lead doesn't corrode. The corrosion is from the other fasteners, whatever they are. I don't think a wood panel is necessary anymore; there just has to be an air gap. I'd be more concerned about where the water is coming from than the corrosion on the panel. Link to comment Share on other sites More sharing options...
John Kogel Posted March 8, 2011 Report Share Posted March 8, 2011 Don't know the exact wording in your report, but if you said the panel "should be mounted on a wood backing" rather than "needs to be", then you wouldn't be relying on a code requirement, and no one could deny it would be good advice. [] That is how I sometimes avoid the "not in the code" rebuttal. Mind you, that doesn't get it fixed, either. [] Brandon mentions the dimples which normally create a small air gap behind the panel. Looks like they are lacking in the pics. Is that a cold basement, and is that moisture from condensation on the cold metal? Link to comment Share on other sites More sharing options...