Mark P Posted October 15, 2010 Report Posted October 15, 2010 I understand that a sub-panel is not to be bonded and the grounds and neutral wires (in the sub) must be separated and the neutrals must be isolated (“floatâ€
Jim Katen Posted October 15, 2010 Report Posted October 15, 2010 Wrong wires to the wrong places. Bare should go left terminal bar. Bonding strap should be disconnect. White wire is is proper now. Sorry clipped writing. Only way make post. Is BF main secure?
Bain Posted October 15, 2010 Report Posted October 15, 2010 How did Mark get his quasi-long-ass post accepted?
Mark P Posted October 15, 2010 Author Report Posted October 15, 2010 I'm having no problems posting, but I don't post as much as most of you... Thanks. I think I understand - ecxept what is "BF Main"
Bain Posted October 16, 2010 Report Posted October 16, 2010 This is a posting test. BF = branch feeder. Edit: A few words apparently make it through.
mgbinspect Posted October 16, 2010 Report Posted October 16, 2010 (You might copy and past posts to WordPad before I submit them, just incase it won't postIf it's .)
Jim Katen Posted October 16, 2010 Report Posted October 16, 2010 BF=Backfed. Must have screw, bolt or clip.
Jim Katen Posted October 16, 2010 Report Posted October 16, 2010 It has white retaining clip. Ah yes. Me no see at first.
Jim Katen Posted October 16, 2010 Report Posted October 16, 2010 Were you on F Troop? Busted. http://youtu.be/bw1ISkzflVs