SNations
    181
Everything posted by SNations
  1. I think you should use boiler plate content. Why waste your time writing the same thing over and over? I don't get that. "I saw signs of extensive mold beneath the roof sheathing at the north side of the attic." What signs did you see? The mold itself? That's not a "sign" of a problem. That's the problem. I think you should be more direct about what you saw. "There's a lot of mold on the roof sheathing in the attic." From a technical standpoint, when I see a lot of mold in the attic it's almost always caused by a particular problem and not just a general humidity issue. Mostly it's a wet crawlspace. So I tell my clients to fix the water problem in the house that's allowing the attic to become too humid. I'm confident that I can usually identify what that water problem is. I think it's great sending your client to EPA for more information about mold remediation, but isn't there a specific website that you can direct them to?
  2. Kurt, I'm with Marc here in not understanding what you mean by needing thermal mass. The concept of mass wall doesn't have much use in Chicago, where winter temperatures get low and stay low. So thermal energy is always going in only one direction -- out. A good and proper amount of insulation isn't going to perform any differently with 3/4 inch drywall or 1/2 inch drywall or even 1/64 inch drywall (assuming such a thing existed), as long as the drywall is airtight.
  3. That's one way to put it, I suppose. But the intention is to not have any induced flow in the secondary loop when that loop is supposed to be off. The intention isn't to not mess up the flow rate when that loop is active. No, I don't think that's right. The secondary loop might be quite large and need a big circulator. You'd simply size the secondary loop circulator for whatever flow and head loss requirement you have -- big or small.
  4. My bible for this stuff is "Modern Hydronic Heating" by Siegenthaler. When you have two closely spaced tees on the primary loop there is very little pressure difference between them. And that's what you want. If the tees are far apart then there's a pressure difference, and that pressure difference will induce flow between the points through the secondary loop. To minimize turbulence in the flow you want at least 8 pipe diameters of straight pipe in the primary loop before the first tee, and at least 4 pipe diameters of straight pipe after the second tee. In Kurt's picture it looks like the primary circulator is bigger than the secondary, so you won't get the short circuiting. But Siegenthaler says that if the closely spaced tees principle is done right the primary circulator doesn't need to be any bigger than the others -- just sized right.
  5. The OP starts like this: "The 2x4 cleats on these 4x4 posts are attached with deck screws. Is that ok?" So how can you possibly say that the cleats were incidental to the OP? From my reading the cleats were the entire point of the OP. And the cleats aren't wrong; they're entirely useless. My point about the bolted connection is that not everything that's wrong is equally bad. Of all the things that a homeowner has to fix and maintain, fixing something that's never going to fail should be pretty low on the priority list.
  6. I don't know why you'd write up the cleats, or the screws in the cleats, or anything associated with them. The cleats aren't doing anything all. And their use even violates a basic rule of mechanical design. You have two load paths of wildly different stiffnesses. One load from the beam and through the bolted connection to the post, then to the ground. That load path is very stiff. It's where all of the load is going. The load path from the beam through the cleat, through the screws, and into the post is extremely flimsy, even if you can install it in such a way that the cleat was originally able to take some load from the beam (which you can't). So that load path isn't taking any significant amount of load because it's so elastic. It's a basic rule that you shouldn't have two load paths really at all, but especially if these two load paths have such different stiffnesses. Because you always want to know where the load is going, and you can't know that with two load paths of different stiffnesses. But in this case the load path through the cleat is clearly so flexible that the cleat is just window dressing and can be ignored. Also, I know it's wrong according to the deck rules, but as far as I can tell no deck has ever failed because this type of bolted connection failed. If anybody knows of such a failure I'd love to hear about it.
  7. Amen, brother. Old Sailor, you've got a nice camera, and I'm sure you like putting it to good use. When I go a long time without my IR showing anything of interest I get a little impatient, and sometimes I start to see things that aren't really there. Over-diagnosis starts to be real problem. There was a study done a few years ago showing that older people with knee pain had MRI's showing problems. Then they took random people off the street with no knee problems and did MRI's. They found that 85% of all people had MRI's that showed problems. So clearly this imaging tool was leading to over-diagnosis simply because it showed something that wasn't perfect. I don't think that a 7 F temperature difference is a problem. And I'm not aware of any epidemic of fires on electric range circuits. And I don't think that your IR images even help to diagnose the source of the "issue". By any chance did you repeat any of your IR imaging after tightening the connection at the breaker? You'd need to do this to help confirm that tightening the connection had done any good at all.
  8. Well I suppose that saying it isn't allowed because nobody has ever proved that it works is not completely unreasonable. Still, I have to believe that somewhere, somehow, somebody on some code-making committee has a theory as to what might go wrong.
  9. I understand that this isn't allowed. But I'd like to better understand why it's not allowed. The solution is to install a single terminal lug, right? So that would put all of the current at just one section of the terminal bar. So clearly the danger isn't that the terminal bar might be overloaded. Electricity flows primarily along the surface of the wire, right? So I don't see the physical problem with load carrying capacity being reduced. Maybe the problem is that splitting up the strands can cause some sort of arc among the different strands. Does that sound right? Anybody know for sure?
  10. Yes. IRC 2012 section 1103.5 (Also IECC 2012 section 403.5) Outdoor air intakes and exhausts shall have automatic or gravity dampers that close when the ventilation system is not operating.
  11. You need a temperature difference between the inside and the outside in order to scan the wall for insulation issues. You don't need a temperature difference to look for water. The evaporation of the water creates its own temperature difference, that you then look for with IR. Or you can let the sun heat the wall, and then let the different heat content of the water show up on IR. This is basically how you'd look for roof leaks.
  12. The difference between natural convection and forced convection is dramatic. I'm convinced there would be a big difference. It's the same idea behind a convection oven, which we know cooks food much faster than a regular oven.
  13. Is that really true? Or does it just transfer the heat to the air more quickly with the blower? If it doesn't put out as much heat, where does the heat go, if not into the room? Out the vent? I'd say it's true. The fireplace is putting out heat at a constant rate. That rate doesn't change based on a blower or not; it depends only on the burner size/configuration and maybe gas pressure. So if heat is being created at a constant rate, then you pretty quickly get to a stead state condition where heat into room plus heat up flue equals heat being created. Heat into room is mostly by radiation. If you add a blower and bring some heat into the room by convection then you've altered the basic equation of total heat = room + flue. But you haven't changed the value of total heat, so you've only changed the values of room and flue. Everything here is a rate (a function of time) so if it transfers heat to the air more quickly with the blower then you get heat in the room at a higher rate and you get heat up the flue at a lower rate. Eventually you'd get heat into the room at such a high rate and heat up the flue at such a low rate that you could use a PVC flue. Then you'd call it a high efficiency furnace.
  14. When clients ask me this type of question I generally reply that the brand of furnace isn't nearly as important as the quality of the folks who install it.
  15. It's safe to say that we've all seen wiring of this lousy quality, and a lot worse. My advice: Don't ever look at something and say to yourself that it can't get any worse than this. Because it can.
  16. Do you know how the roof was damaged?
  17. I think it depends on the code. IRC = yes UPC = no Chicago = ??? IRC P3103.6 Extension through the wall. Vent terminals extending through the wall shall terminate not less than 10 feet (3048 mm) from the lot line and 10 feet (3048 mm) above the highest adjacent grade within 10 feet (3048 mm) horizontally of the vent terminal. Vent terminals shall not terminate under the overhang of a structure with soffit vents. Side wall vent terminals shall be protected to prevent birds or rodents from entering or blocking the vent opening.
  18. Every client is looking for something different from their home inspection. Some want a thorough inspection so they can negotiate. Some want not just a thorough inspection to find problems but they want to learn about the house too. So they want to know what's right and to understand how things work. Those are the clients I like best. Some clients consider a home inspection to be just something they have to do, almost like paying a tax. So they just try to find the cheapest inspection they can, and seem to pay little attention to the results short of almost literally "Will it fall down?". Those are the worst clients, but since they're shopping primarily by price I avoid most of them. Everyone has their own motivation.
  19. The two lugs on the left side are the hot side line and load. The two lugs on the right side are neutral side line and load. I don't see where the neutral is hooked to the hot bars. I'm with Katen: all I see is the wrong color wire. Fusing the neutral is wrong, but having the neutral on a manual disconnect isn't wrong. Is it?
  20. I pay 8.5 including all taxes and fees. Congratulations Chad. It looks great. Do you spend much time just watching the meter spin backwards and smiling? In my town there is currently a big controversy because the village board is ending an electricity aggregation program that purchased only green energy. When they put it back up for bid this year they decided that brown energy was cheaper and so went that route. Many people are not happy.
  21. Jim, this is interesting. Where I live the counter staff won't tell you anything more than which version of the code they enforce.
  22. I don't understand this part. It sounds more like an indictment of a poorly installed flue than a problem of running the flue and intake to different areas. Am I missing something?
  23. There's an interesting new Building Science Corporation document -- BSI-075 -- that just came out last week. It's making the argument that this is from air leakage (exfiltration) above the neutral pressure plane. At the corners of the building something, probably wind pressure, is causing air leakage also. It's an interesting article (but aren't they all from BSC).
  24. Yes, 303 therms is in the ballpark for 33 winter days for a worse than average home with little insulation and high air leakage, which sounds like what you've got. Plus, your furnace isn't working right. It shouldn't start up the immediate second after it shuts down.
  25. So the engineer measured the crack (how long did he have to go to school to learn how to use a ruler?) and told you to contact somebody who actually knows what he's doing? You should ask for your money back.