  1. Originally posted by patt

    Wasn't thinking straight about the siphoning?

    How would that protect against overflow? Do you mean overflow at the standpipe or at the washer?

    At the washer, if the discharge valve was stuck open and water continued to try fill the bowl.

    I don't think that any standpipe would guard against that, no matter what the height.

    For fun I went to the GE site and they only mention 30" minimum, no maximum stated.

    http://products.geappliances.com/ApplPr ... TWN4250DWS

    NOTE: If drain hose facility

    does not meet 30" minimum

    height requirement, thread

    drain hose through supplied

    anti-siphon clip U and mount

    to cabinet back as shown

    Those are the abbreviated instructions for doofuses. Here's a full set of instructions, check out page 18, it say 96 inches, just like Maytag & Whirlpool:

    https://www.ptsem.edu/uploadedFiles/Ope ... ctions.pdf

  2. Just thinking, shouldn't the top of the standpipe be below the top of the washing bowl, for overflow protection?

    If so, then there's no mention of it in the codes or in the manufacturers' installation instructions.

    How would that protect against overflow? Do you mean overflow at the standpipe or at the washer?

  3. So the trap might be above the washer?

    Then you have to worry about siphoning.

    I think they're doing it 1. for convenience, 2. Possibly there is standard for length of discharge hose.

    The whole point of the standpipe is to provide an indirect waste receptor, which makes siphoning unlikely.

    It would be much less convenient to have to install a sewage ejector.

    Supplementary hoses are easily available.

  4. The UPC, Section 804.1 sez:

    No trap for any clothes washer standpipe receptor shall be installed below the floor, but shall be roughed in not less than six inches and not more than eighteen inches above the floor.

    Why do you suppose there's a maximum height of 18 inches?

    Washing machine manufacturers all (nearly all?) allow their washers to be installed with standpipes up to 96 inches above the bottom of the washer. With a 30-inch standpipe, that would put the trap about 66 inches above the floor. If it's ok with the manufacturers, what problem is the UPC trying to address?

    I'm thinking of basements where the sewer line might exit the basement at three or four feet above the floor.

  5. Seems like I remember reading about these solo walls in bathrooms need to be ventilated in order to not get interior moisture damage. Is that true?

    I've never heard that. If you find the source where you heard it, please pass it on.

    FWIW, I've seen a lot of houses and apartments torn apart and I've never seen a particular problem with condensation in interior walls.

  6. If you look carefully at the first picture, the crack begins and ends in the middle of the concrete, with no other cracks radiating from it. The concrete had to have been plastic when that crack formed. I've had forms blow out during pours and as the mass of concrete starts to slump, it can create cracks just like that.

  7. Most of the damage seems to be in the built-up, double-thick sections. There were a lot of shingles that did this in the 90s and early 2000s but I haven't seen it in a while. If the fissures are really just limited to the thickened sections, it doesn't seem to cause performance problems.

    I can't tell much else from your tiny little pictures.

×
×