RSpermo
    42
Everything posted by RSpermo
  1. Erby, As you know a lot of aspects go into sizing a HVAC unit. I am presently air conditioning my 4100 sq ft 2 floor house in south central Texas mostly with a 3 ton unit. I do have a 4 ton unit that is zoned that comes on very sparingly. As others have said the insulation, the infiltration rate, the sensible/latent split and other aspects must be considered. Have a reputable HVAC contractor run a load calculation. As least then you will have a recognized number.
  2. I don't think it is the lid switch. I just replaced my lid switch because the washer would stop when it got to the rinse cycle. Moving the knob still had no effect. I think when the lid switch goes it shuts down the rinse and spin cycles completely.
  3. Let's look at some simple math. Before the math is the attic ceiling insulated? I will assume it is and just concentrate on the 2 uninsulated walls. If the 2 walls are 40 feet long and 8 feet high that would be a total of 640 sq ft of uninsulated walls. Using a formula of BTUs of heat lost = U factor (assume .33) x sq ft (640) x temperature difference between indoors and outdoors (50 degrees), the answer is 10560 btus of heat lost per hour or 253,440 btus of heat lost per day which is 2.5 therms. For 30 days you have lost 75 therms right there! I am also betting your attic/ceiling is insufficiently insulated.
  4. I think the guy is incompetent and has opened himself up to lawsuits by the home owner! He is trying to sound like a competent HVAC contractor but has failed to do so! I would charge $250 - $300 to do a load calculation (requires a lot of onsite measurements, etc).
  5. Anyone interested in doing an inspection in Lancaster, Va for a 3800 sq ft home? It is for my daughter's father-in-law. Call Bob @ 210 385-1209
  6. I do blower door leakage tests in south Texas in the summer. I have used my IR camera during the test. Its benefit is that with the IR camera it does highlight the hot air that is being pulled into the inetrior through leakage holes. Would I buy an iR camera just for this purpose? No! I would only buy an IR camera if I was willing to get proper training and I had some valid uses for it.
  7. Phillip - Exactly why I went out and earned my Texas HVAC Contractor's license. I can now give my clients a more thorough inspection. By the way taking static pressure only requires a "pitot tube" and a pressure measuring gauge.
  8. Phillip, Have you checked the static pressure in all configurations (different dampers opened and closed)? It may very well be that in the worst case the static pressure is approximately .5"WC.
  9. I recently installed a damper and zoned system with a barometric bypass duct from the supply plenum to the return plenum. The bypass duct functions basically on the static pressure in the supply plenum. I took the static pressure and got .55"WC. That was my goal - around .5. I installed 3 dampers and when one zone is called for it goes full open and the other 2 still remain 50% open. So I think the bypass duct may depend on what the dampers do when that zone that is not the primary zone. You also have to ensure that the bypass duct does not put too much cold air back into the return system. By the way I used 800 KwHrs less this July than last (temps about the same - high 90s - 100 all month).
  10. I would ask Carrier if the coil and the condenser are allowed to be used (matched) together. The final answer rests with the manufacturer.
  11. The best way to size a HVAC system is to do the full manual J, S and D. Short cuts and other methgods can lead to mis-sizing.
  12. Mike, I just talked to the head code compliance officer for HVAC for the state of Texas at the Department of Licensing. In Texas only the homeowner or a licensed HVAC technician can repair (seal ducts with tape or mastic). Anyone else that repairs ducts would be in violation of the state licensing laws and subject to a large fine. While I have no idea what the laws are in Va I would certainly check before I do any more repairs.
  13. Nolan, I am interested in the protocol that this "auditor" follows. Would you please post after the audit exactly what the "auditor" did.
  14. There are many companies in the weatherization business that are having success by blowing cellulose into the wall cavities from the exterior. I have seen it done in 40 - 50 year old houses. By the way while you may have R-13 insulation in the walls your wall is probably closer to R-8.
  15. I would be careful in calling a unit too small if I had not done Manual J calculations. You really need to address alot of factors (insulation, house siting, overhangs, windows, etc) before calling it undersized. Oversized is more of a problem especially in regards to removal of moisture.
  16. The first thing you should do is have someone do a Manual J calculation so you know what size your house really needs. There is no need to guess on unit size when calculations will give you the correct answer.
  17. Rick, I am a BPI Building Analyst, RESNET Certified Rater and licensed (Texas) Home Inspector. I do "energy audits". I do not determine how extensive my audit will be until I talk to and visit the client at their house. I find out what problems the home owner has (large bills, drafts health problems Etc) and/or what the owner's goals are before I start any audit. While I cando blower door, suct blaster or IR camera tests in many cases they are not warranted. For example, I was at a home with year round high electric bills. The home owner was running 2 pool pumps 24 hours a day. I showed him how much they were costing him ($200/month) and told him to put the pumps on a timer whcih could save $120/month. No needfor a blower door! There is not much call for energy audits but I do have a good business in conducting Energy Star Certifications for new construction. This requires a RESNET Rater Certificationand equipment.
  18. I am not going to comment on closed versus open cell foam but I would like to comment on using foam insulation to retrofit a home. When insulation is the only factor you consider during your retrofit you are forgetting that the house is a system. If you change one thing it has an impact somewhere else. For example if you foam the rafters and do nothing to the central air conditioning unit (which is probably oversized in the first place) you can run the risk of not getting the humidity/moisture out of your house. While I like foaming the rafters in new construction where the A/C system is sized properly I would be wary of during only one thing and not the other.
  19. Just remember this Watts/Volts = Amps or Watts = Volts x Amps or Volt = Watts/Amps
  20. Have him show you his Manual J and Manual D calculations for your house.
  21. My IR camera has not produced any more income to my home inspection business, However, it has increased my energy analysis business and just last summer got me a job that paid me 4 times what I paid for the camera. Without the IR camera I could not have gotten thia lucrative job. In addition, those homes that I visited to fulfill my IR contrcat job couls easily become home inspection clients at a later date.
  22. The code actually says - one EXIT door required - all EGRESS doors shall be openable from the side from which egress is to be made without the use of a key or special knlwledge or effort. Code inspectors in my area interpret it to mean all EGRESS doors cannot have a double keyed lock. I agree with Jim.
  23. There is no limit to the number of outlets on a circuit. However, you need to calculate the amount of amps you plan on drawing on that circuit. Since it is in a garage there may be work going on. If you have workshop in the garage a circuit could get some heavy use with more than one power tool running at the same time. Also you may want to adda 20 circuit if you have a workshop. In addition, make sure all outlets in your garage are GFCI protected. By the way it is not a sub panel but is a distribution panel.
  24. IAW the 2006 IRC (E3305.4) a panelboard cannot be in a bathroom. A panelboard can be a closet but not a clothes closet. In addition the panelboard requires a 36 inch space in front of it and at least 30 inches wide.
  25. The TPR drain line if it is going to be PVC must be CPVC. This drain must operate separately so the water heater drain cannot empty into it.